Breaking capacity
Encyclopedia
Breaking capacity or interrupting capacity is the current that a fuse
Fuse (electrical)
In electronics and electrical engineering, a fuse is a type of low resistance resistor that acts as a sacrificial device to provide overcurrent protection, of either the load or source circuit...

, circuit breaker
Circuit breaker
A circuit breaker is an automatically operated electrical switch designed to protect an electrical circuit from damage caused by overload or short circuit. Its basic function is to detect a fault condition and, by interrupting continuity, to immediately discontinue electrical flow...

, or other electrical apparatus is able to interrupt without being destroyed or causing an electric arc
Electric arc
An electric arc is an electrical breakdown of a gas which produces an ongoing plasma discharge, resulting from a current flowing through normally nonconductive media such as air. A synonym is arc discharge. An arc discharge is characterized by a lower voltage than a glow discharge, and relies on...

 with unacceptable duration. The prospective short circuit current which can occur under short circuit
Short circuit
A short circuit in an electrical circuit that allows a current to travel along an unintended path, often where essentially no electrical impedance is encountered....

 conditions should not exceed the rated breaking capacity of the apparatus. Otherwise breaking of the current cannot be guaranteed. Breaking capacity current corresponds to a voltage, so an electrical apparatus may have more than one breaking capacity current, according to the voltage. Breaking current may be stated in terms of the total current or just in terms of the alternating-current (symmetrical) component. Since the time of opening of a fuse or switch is not coordinated with the reversal of the alternating current, in some circuits the total current may be offset and can be larger than the alternating-current component by itself.

Choosing breaking capacity

Calculating of the required breaking capacity involves determining the supply impedance and voltage. Supply impedance is calculated from the impedance of the elements making up the supply system. Customers of an electrical supply utility can request the maximum value of prospective short circuit current available at their point of supply. Networks involving multiple sources of current, such as multiple generators, electric motors, and with variable interconnections may be analyzed using computer software. A system study will generally consider the maximum case of additions of generation and interconnection out to some projected horizon year, to allow for system growth during the useful life of the studied installation. Since practical calculations involve a number of approximations and estimates, some judgment is required in applying the results of a short-circuit calculation to the selection of apparatus.

Some applications have low short circuit current so any fault current protector will suffice. This is typical for supplies from miniature transformers as used in control circuits. In large systems such as industrial power centers or utility networks, fault currents can be very high and selection of a suitably rated device is important.

Breaking capacities

Miniature circuit breakers and fuses may be rated to interrupt as little as 75 amperes and are intended for supplementary protection of equipment, not the primary protection of a building wiring system. In North American practice, approved general-purpose low-voltage fuses must interrupt at least 10,000 amperes and certain types useful for large commercial and industrial low-voltage distribution systems are rated to safely interrupt 200,000 amperes. The rating of power circuit breakers varies according to the application voltage; a circuit breaker that interrupts 50,000 amperes at 208 volts might only be rated to interrupt 10,000 amperes at 600 volts, for example. Direct-current systems such as used with batteries present a special problem because current does not naturally reverse on each half-cycle, making interrupting of faults more difficult.
The source of this article is wikipedia, the free encyclopedia.  The text of this article is licensed under the GFDL.
 